How to write the fuel and product exergy balances in the cascade heat exchanger in the cascade refrigeration system?
Relevant answer
Answer
Dear Cenker Aktemur,
According to information provided by Saeed Sayadi, there is a complication when total exergies of the flows are used to define fuel and product in a heat exchanger. Besides the dependence on the reference ambient temperature, there is the inconvenience of applying the disaggregation of exergy into thermal and mechanical components. Such disaggregation has already been criticized in the literature due to potential arbitrariness.
On the other hand, there are proposals in the literature to define fuel and product in heat exchangers without the aforementioned problems. Please look for the UFS and A&F Models, which were designed for exergo-economic and exergo-environmental analysis of refrigeration and heat pump systems.
Best regards,
Atilio.
  • asked a question related to Refrigeration & Air Conditioning
Question
2 answers
I need to know the entire design procedure of the heat pump. How the compressor is selected based on the refrigerant and temperature? How each and every component of a heat pump is designed and the theoretical calculations behind them.
Relevant answer
Answer
Remember that selecting the right compressor is just one aspect of designing an efficient heat pump system. The entire system, including components like the heat exchanger, air handler, and controls, must work together seamlessly to achieve optimal performance and energy efficiency. Therefore, it's essential to take a holistic approach to heat pump system design and consult with professionals when necessary.
  • asked a question related to Refrigeration & Air Conditioning
Question
8 answers
I'd like to hear your thoughts and experiences on using nitrogen in place of R32/R410/R22 refrigerant in a residential air conditioner refrigerant system.
  • 18000BTU Air Conditioner Capacity
  • 350 psi Nitrogen Standing Pressure
The system is sealed, and the compressor is given power.
Relevant answer
Answer
Aside from the obvious required phase change temperatures, for any refrigerant one needs to consider the contaminants, physical, metallurgical, sensor ranges, and chemical interactions - especially lubricant oils ( like Polyester POE Oil ) from the compressor and the seals. It isn't simply the refrigerant itself, there is a lot of complexity, especially over the total lifetime of the system. There is also a huge thermodynamics design challenge involved, heat capacity and transfer (like surface to volume ratio and fluid flow (gases and liquids ) determines the dimensions and material choices of everything.
  • asked a question related to Refrigeration & Air Conditioning
Question
4 answers
An air-cooled evaporator will be placed in a room and the evaporator temperature will be -40oC. What should be the air temperature to and from the cold room to the evaporator? The screenshot is attached. Thank you.
Relevant answer
Answer
Ali D. Salman thank you very much. In this case, will the temperature of my room be -28oC or -34oC?
  • asked a question related to Refrigeration & Air Conditioning
Question
4 answers
In Design of experiments,
Response Surface Methodology,
If I conducted Experiments with  variables different level example 3 factors and 3 levels, 15 runs,
Under open Atmospheric Condition,
How can I validate the model,
Because For 15 runs adopted different Atmospheric Condition,
Is there any possible solutions,
Please Suggest,
Thanking you.
  • asked a question related to Refrigeration & Air Conditioning
Question
2 answers
why I need to enter the mass flow rate in stream 1 in aspen plus ? For example, I entered the mass flow rate as 1 kg / sec. I want to change it according to the cooling load of the evaporator but it remains as 1 kg/sec. Can you explain it clearly please ?
Relevant answer
Answer
Use parametric or conditional study, atleast one parameter should be unknown. For your case it might be two. So you need to fix that. Also check adding other stream too.
  • asked a question related to Refrigeration & Air Conditioning
Question
11 answers
How can I calculate boiling point of LiBr-H2O according to LiBr concentration ?
Relevant answer
Answer
Pressure-temperature-concentration can be available in Heat and mass transfer text books. Every chemical temperature and concentration is discussed.
  • asked a question related to Refrigeration & Air Conditioning
Question
11 answers
Variable-speed-compressor refrigeration systems were examined by many researchers for minimizing energy consumption. The results were interesting. However, this technique may be possible for new designed systems. My question is about systems which are in service right now.
Relevant answer
Answer
Use the frequency invertor .
  • asked a question related to Refrigeration & Air Conditioning
Question
3 answers
A Vapor Compression Refrigeration system has a 281W, 50 Hz compressor with displacement 11.1 cm3/rev. 50 Hz compressor has RPM 3000. The discharge pressure is 13.5 bar, the suction pressure is 0.13 bar. Subcooled liquid temperature is 32°C, superheated temp is 54.4°C and evaporator temp is -23.3°C. Thus, the mass flow rate can be calculated to be 2.2 kg/min. That gives heat removed from the evaporator as 254kJ/min. Thus, to cool a load of 100 kJ, it takes only 23 sec? But in reality, it takes somewhere around 1 hr to cool the object with a 100 kJ load. How to approach this problem?
Relevant answer
Answer
First, the heat removed you mentioned above is for steady state condition analysis. Second, your calculation is probably ideal condition. Let's assume your refrigeration system is already ideal condition.
Then, is your 100 kJ load is your experiment? if yes, is it perfectly thermal insulated?
In real world, there always small heat loss when you use insulation material. So you need to consider this heat loss. How? The simple way is to analyze the transient temperature increasing when your object is cold and without cooling system (your refrigeration system is off).
  • asked a question related to Refrigeration & Air Conditioning
Question
7 answers
I am trying to model a single-effect absorption refrigeration system using LiBr/H2O in Aspen Plus. Who can help me model the absorption cooling system? Please send a private message.
Relevant answer
Answer
Sampath Suranjan Salins I am talking about aspen plus not ansys fluent.
  • asked a question related to Refrigeration & Air Conditioning
Question
7 answers
Dear all,
I want to find enthalpy and entropy of Libr-water solution at 25 oC  temperature and 1 bar pressure. Is there any standard formula available for calculating enthalpy and entropy of LiBr-water solution having various concentration percentage of LiBr in solution? 
Relevant answer
Answer
A very useful link to find the thermodynamic parameters ( △G°, △H° and △S° ) form experimental data.
  • asked a question related to Refrigeration & Air Conditioning
Question
2 answers
By knowing the specific volume on the inlet and on the outlet, is it correct to assume an average of those two specific volumes?
Relevant answer
Answer
Thank you for your answer Mr. Rocha,
Answering the question, yes, it is expected to have a constant pressure.
Kind regards
  • asked a question related to Refrigeration & Air Conditioning
Question
1 answer
Although there are already studies in the literature but not much , the use of potassium formate/water or potassium formate+LiBr/Water are not available in the commercial sector for absorption refrigeration systems? what is the actual reason ?
Relevant answer
Answer
Dear Cenker Aktemur I found a report on the use of potassium formate/water (see attached) in which some severe corrosion problems were observed. They are listed on p. 21 of this report:
Besides very good results in thermal aspect, Freezium and Pekasol 50 exhibits some problems in material compatibility. This could be summarized as:
- We have observed very aggressive reaction to zinc;
- Copper pipes in contact with copper were covered by blue/green (somewhere some white layers formed at the top of this coating);
- All steel surfaces where coating was damaged corroded significantly;
- Some gaskets in valves were damaged and valves leaked.
  • asked a question related to Refrigeration & Air Conditioning
Question
3 answers
Although there are already studies in the literature but not much , the use of potassium formate/water or potassium formate+LiBr/Water are not available in the commercial sector for absorption refrigeration systems? what is the actual reason ?
Relevant answer
Answer
Dear Cenker Aktemur I'm not an expert in this field and therefore cannot provide you with a final answer. However, I found a report on the use of potassium formate/water (see attached) in which some severe corrosion problems were observed. They are listed on p. 21 of this report:
Besides very good results in thermal aspect, Freezium and Pekasol 50 exhibits some problems in material compatibility. This could be summarized as:
- We have observed very aggressive reaction to zinc;
- Copper pipes in contact with copper were covered by blue/green (somewhere some white layers formed at the top of this coating);
- All steel surfaces where coating was damaged corroded significantly;
- Some gaskets in valves were damaged and valves leaked.
  • asked a question related to Refrigeration & Air Conditioning
Question
2 answers
We have been numerically investigating the thermal-fluid characteristic of sCO2 laminar flowing in a 0.5 mm diameter circular microtube in upward direction. Depending on sharp density change along the tube, this case can be admitted as a compressible flow. When applied pressure-based solver option, the pressure firstly decreases until a certain point along the tube, then increases towards the outlet. So, this situation is impossible. Can this situation result from pressure-based solver? Can it be fixed by using density-based solver? I would like to be grateful if you could share your recommendations. (Boundary conditions: mass flow inlet, pressure outlet (75 bar), constant wall heat flux)
Relevant answer
Answer
Dear Sir, thank you for your reply. We have already defined the properties of the sCO2 by using Fluent Console (NIST tables for CO2 is current in the Fluent database). Although the entire graph is very reasonable, the pressure change along the flow direction is interesting as seen in the attached file. When calculated theoretically (considered friction depending on both wall shear and momentum change) by using Ansys data (wall shear stress, density, axial velocity, etc.), the pressure drop is found as expected (full decreasing along flow direction).
  • asked a question related to Refrigeration & Air Conditioning
Question
5 answers
How can I theoretically calculate the mass flow rate of nanofluids such as WATER+AL2O3 ?
Relevant answer
Answer
Equation of Nanofluids
Density .........................(1)
ρ_nf = (1-φ)ρ_f + φρ_s
Heat Capacitance ..............................(1)
(ρC_p )_nf= (1-φ) (ρC_p )_f+𝛗(ρC_p )_s
Thermal Expansion Coefficient .............................(1)
β_nf = (1-φ)β_f + φβ_s
Thermal Diffusivity ..............................(1)
α_nf =Κ_nf/(ρC_p )_nf
Effective Thermal Conductivity ...............................(1)
Κ_nf/Κ_f = (Κ_s+2Κ_f-2φ(Κ_f-Κ_s))/(Κ_s+2Κ_f+2φ(Κ_f-Κ_s))
Viscosity ..................................(1)
Brinkman model
µ_nf = µ_f/〖(1-φ)〗^(2.5)
Pak and Cho correlation
µ_nf = µ_f ( 1+39.11φ+533.9φ^2 )
Reynolds number
Re= 4Ϻ/(π.D.µ)
Ϻ= (Re.π.D.µ)/4;
where,
[M= Mass flow rate]
[Re= Reynolds number]
[D= pipe diameter]
Reference
1. Combined convection flow in triangular wavy chamber filled with water–CuO nanofluid: Effect of viscosity models
  • asked a question related to Refrigeration & Air Conditioning
Question
9 answers
How can concentration in terms of rich and poor be affected by adding nanoparticles to LiBr-Water?
Relevant answer
Answer
Dear Kenkar,
In diffusion absorption coolers regarding to the heat performance of the system, ammonia/water couple with alumina (Al2O3) particles in nano-size can be a better option. It can provide better absorption of heat from the generator and faster evaporation of the cooler from the cooling/absorption fluid. Considering the effect of fluids containing nanoparticles the connection units of the heat transfer in the system operation time of the system might be reduced due to shorter heat transfer periods.
Ashish
  • asked a question related to Refrigeration & Air Conditioning
Question
10 answers
I wanted to know if we can store frozen cells in -80 C refrigerator. These cells are stored in liquid nitrogen tank (-200 C) as of now. But as liquid nitrogen vaporizes, we need to keep refilling the tank every two months. Since, the university is going to be under lockdown due to COVID-19, we will not be allowed to enter labs or be able to order new liquid nitrogen. So will it be feasible to store these frozen cells at -80 C for the coming 3-4 months?
Relevant answer
Answer
Hi Adity,
I think you can keep your cells in -80 for several years. However I strongly suggest that after the Covid-19 situation, cultivate your cells again and prepare your nitrogen source from fresh culture. Do not put them directly into Nitrogen Tank.At least make an experiment first. For example, put some cryovials into liquid nitrogen and after couple of days, cultivate them. If they are alive you can transfer your cells into liq. nitrogen tank too.
The first concern for me is contamination.
Second, depen on my experiences, I realized that cells dye if they stay first too long in -80 and consequenlty transfered to nitrogen. With too long, I mean more than 2 months.
Cells are normaly alive -80 for years. I agree with that. However, if you put these cells from -80 after 3 months into liquid nitrogen, unfortunately cells may dye. That occured to us several times. That's why we never keep our cells more than 3 weeks in -80 after crypreservation protocol. If we forget them in -80, we use them but never put them into nitrogen tank again.
I hope your cells will be Ok.
Good luck!
Cigdem
  • asked a question related to Refrigeration & Air Conditioning
Question
6 answers
I am starting my master thesis now and having trouble with create a MATLAB codes. Can anybody help me to create a matlab code for  water heater, AC and clothes dryer and control some critical loads(lighting etc.). I just want to learn how to start and create a codes as an example. 
Best Regards, 
Relevant answer
Answer
Dear all
Any body implement Model predictive control based EMS ?
i need help
  • asked a question related to Refrigeration & Air Conditioning
Question
6 answers
I have designed a compression refrigration cycle with R134a and the pressure of the condenser is about 10 bar and the pressure of the evaporator is 1.8 bar. 
I want to know what is the evaporating and condensing pressure range? 
Relevant answer
Answer
The log P-h diagram of R134a refrigerant sented in attachment. you can use this diagram to design. Note that compression refrigeration cycle designing depend on to several parameters. main parameters is ambient temperature and cooling load. Also you can use coolpack software to design refrigeration cycles.
  • asked a question related to Refrigeration & Air Conditioning
Question
14 answers
Hello everyone! 
I am just about to take part in a refrigeration system design competition but unfortunately it is my very first time stepping in the real world of engineering & I do not know exactly what are the steps of designing a one-stage vapor compression refrigeration cycle. The system I should design must be able to handle the followings:
1-cooling down a 50 L of water storage from 28 C to 7 C at a minimum time duration.
2- Constraint: compressor power must not exceed 600 W!   
I would deeply appreciate you if you could help me through.
Relevant answer
Answer
This is a heat transfer rate maximization problem in the evaporator , in which you have to find an evaporator with the maximum LMTD which means the highest efficiency. Theoritically you can cool down the water as fast as you want but you have design restriction such as refrigrerant inlet temp to the evaporator. In the best scenario the refrigerant inlet temp to evaporator cannot be higher than 2c for your design case and it leads to local water solidification which acts as an insulator. To solve this problem you can recirculate water in tank or add antifrost to tank if you are not using it for sanitary purposes. Higher evaporator efficiency inflicts alot more costs.
  • asked a question related to Refrigeration & Air Conditioning
Question
5 answers
Dear all,
I am trying to find cooling power to weight ratio for vapour compression and vapour absorption chiller. If you have any relevant information please share.
Thank you for your support.
Relevant answer
Answer
Cooling power is the amount of energy/sec require to derive the cooling system like vapor compression or vapor absorption and mass flow rate of refrigerant is directly proportional to the cooling capacity of system.so the cooling power and mass ratio can be calculated by using refrigeration table
  • asked a question related to Refrigeration & Air Conditioning
Question
7 answers
refrigeration technologies
Relevant answer
Answer
Ejector refrigeration systems and absorption chillers are the most common systems which use heat sources instead of electricity. please check the following articles:
  • asked a question related to Refrigeration & Air Conditioning
Question
4 answers
Charge minimization is essential for flammable refrigerant RAC system designs. One of the solutions is using small, mini or micro channel heat exchangers. Nowadays, cost-effective air coil heat exchangers with small and mini channels have been becoming widely available. However, more circuits must be adopted to reduce the pressure drop of refrigerant flow in the smaller channels.
An example from our RefrigLab cloud eTools ( www.refriglab.com ) client is used with their kind permission to show the effect of coil tube diameter on the unit charge and coil circuiting number. An air cooler unit with propane/R290 as refrigerant employs a 18cc/R290/MLBP/POE-600cc compressor operating for 3-7 deg.C of cold product storage at 35 deg.C/65%RH ambient condition. The unit cooling capacity and energy efficiency are about 1.6kW and 2.0 respectively. Four copper tube size coils were used for the exercise during the developing stage, 9.52mm (3/8"), 7.94mm (5/16"), 7mm (0.276") and 5mm (0.197") outer diameter.
The obtained results show that, with the decrease in the coil tube outer diameter, propane/R290 charge quantity (left chart in the title image) decreases linearly, but the evaporator coil circuiting number (right chart in the title image) increases sharply. In addition, the difference in the cooling capacity and COP is less than 1% among the different tube coils.
If you are interested in our cloud eTools, please Register at the website www.refriglab.com and take free trials. This document is a copy of my LinkedIn post at the following link and you may access my other posts at LinkedIn.
The results shown above and attached are for your comments. Are there any other issues with the use of mini/micro channel heat exchangers in refrigeration and air-conditioning units?
Relevant answer
Answer
Hi, Rahul
The diagrams show the effect of coil tube diameter on unit refrigerant total charge and coil circuiting number with identical compressor size ( compressor displacement, rotation, oil type and oil charge quantity.)
Hopefully this helps.
  • asked a question related to Refrigeration & Air Conditioning
Question
4 answers
It's vital to optimise the refrigerant charge for refrigeration and air-conditioning units. The attached are charging curves of a typical air cooler R290 unit with 5mm OD tube air coils based on modelling with RefrigLab cloud eTools (www.refriglab.com):
Fig(a): Both COP and cooling capacity are maximised with R290 charge of 140-148g. Refrigerant R290 entering into TEV is subcooled (SC>0, quality Xinlet=0, no bubbling) with charge >=130g.
Fig(b): Condensing and evaporating temperatures increase with the charging while suction vapour superheat decreases first during the undercharged period and increases slowly during the later overcharged process.
Fig(c): Compressor stores nearly half (42%-53%) of total R290 charge during the undercharged but condenser coil holds the largest during the last overcharged stage.
Any suggestions or comments on the modelling?
This post for discussion is a follow-up to my previous ones at LinkedIn:
Relevant answer
Answer
Thank you, Prabakaran! I will look at some of them that I did not before.
There are different coolers/freezers. Some products just operate at relatively stable ambient and product conditions and no pull-down operations are needed,, some require quick chilling/freezing, and some require minor pull-down capacity. Therefore, it depends on what your product designs require.
RefrigLab cloud eTools (www.refriglab.com) provide components designs and unit overall performance tuning including pull-down, ambient adaptation, charging optimising etc.
  • asked a question related to Refrigeration & Air Conditioning
Question
3 answers
Hello scholars,
Presently am working on a design of an evaporative condenser for a refrigeration application.
Inputs available with me:
1.Typical ambient DBT & Relative Humidity for the region of application .
2. Atmospheric pressure.
3. Heat load/Condensing Load.
4. Design Condensing Temperature( 5 deg.C to 10 deg.C Higher than WBT).
5.Mass flow of refrigerant.
The evaporative condenser will be applied in an static ambient & no fans will be deployed, unless otherwise if technically required.
A pump is used to spray the water onto the evaporative surfaces to enhance evaporation.
Questions:
1. How to estimate the evaporative surface area required?
2. How to estimate the pump flow rate required?
3. How to estimate the rate of water to be refilled/ rate of water evaporation?
Looking for useful correlations/articles which can guide me for the design.
Please note:
I am designing it for a 3.5 kW Condensing load application.
DBT for the region is 45 deg.C & RH is 30%.
  • asked a question related to Refrigeration & Air Conditioning
Question
10 answers
How does a SLHX impact refrigerant charge?
The attached diagram shows the results from a typical air cooler's R290 unit: The unit R290 total charge decreases with the increase of SLHX vapour superheat. When the superheat is greater than 20K, the unit R290 total charge is less than 150 grams. With the increase in SLHX's heat transfer area (e.g., flow channel length), superheat of suction port refrigerant vapour increases so the refrigerant mass dissolved to compressor lubricant oil decreases while the refrigerant quantities stored in condenser and evaporator 5mm OD coils have relatively small changes as displayed in the diagram.
This is part of my LinkedIn Posts about SLHX (Suction Line Heat Exchanger) with the link https://lnkd.in/gPbb8E7 and https://www.linkedin.com/feed/update/urn:li:activity:6445911044706697216 and about refrigerant charge minimisation with the link https://lnkd.in/g68uaJW based on the cloud eTool calculations ( www.refriglab.com ). Please click these links for further details. Your critical comments will be much appreciated.
Is a SLHX really required in a low charge RAC unit?
Relevant answer
Answer
The solubility of refrigerant like R290 in POE32 for example can be calculated using the compressor suction temperature and pressure, i.e., the function equation y=f(x1,x2). The solubility equations are available from lubricant companies or compressor companies. Hopefully this helps.
  • asked a question related to Refrigeration & Air Conditioning
Question
21 answers
Usually mass transfer is described with the following equation: m = A*U*dc, where dc is the difference in concentration of a component between two phases, or a phase and the interface...
Fick's law of diffusion also uses the difference in concentration.
In reality, the driving force for mass transfer is the difference in chemical potential, which depends not only on the concentration but also on temperature and pressure.
Why then is the difference in concentration usually applied? In which cases can/can't it be applied?
Relevant answer
Answer
Dear Tom,
thank you very much for all the references, comments and reflexions :)
Here I found a document that relates the cocentration gradient in the Fick law with the chemical potential gradient, but, as you said, I think it is obtained using analogy...
Regards,
Cristina
  • asked a question related to Refrigeration & Air Conditioning
Question
4 answers
We have recently designed an experimental setup to investigate the detailed thermofluidic mechanism of near-critical CO2. We need to pump, ensuring low flow rate, high operating pressure and also smooth flow (eliminate pulsation effects, caused by the pump, in the test section). Our specifications are 20 ml/min flow rate, 1-2 bar discharge pressure, 8 MPa operating pressure. I would like to be grateful if you could recommend the manufacturers. Best Regards.
Relevant answer
Answer
Thanks a lot, Dear Gholampour, Eidan, and Kareem. We decided to use a pulse free pump with an accumulator compensating any pressure wave.
  • asked a question related to Refrigeration & Air Conditioning
Question
12 answers
It's vital to minimise the flammable refrigerant charge quantity while retaining the high energy efficiency of refrigeration and air-conditioning units. Here are the tips that I list for your suggestions and comments:
1. Select smaller tube coils for evaporator and condenser. If using 5/8", 1/2", 3/8" or 5/16" OD coils now, for example, you may try 7mm, 6mm or 5mm OD coils instead or go straight to micro channel coils.
2. Choose a compressor with less oil charge quantity and/or more viscous lubricant oil type. With the same cooling capacity and/or COP, different brand compressors may require different lubricant oil type and/or different oil charge quantity.
3. Size a suction line heat exchanger with highly enhanced and compact liquid channels to have less liquid refrigerant store and achieve adequate vapour superheat so as to reduce the refrigerant mass dissolved to compressor lubricant oil.
4. Install the filter/dryer (and receiver if required) to have a bottom/lower outlet port.
5. Use smaller liquid tubes from the condenser outlet to expansion valve or CAP tube inlet.
This is a copy of my post on LinkedIn ( https://www.linkedin.com/pulse/tips-minimizing-hydrocarbon-other-refrigerant-charge-rac-jeff-wang/ ) about the applications of cloud eTools provided by www.refriglab.com . Your additions, suggestions and comments will be much appreciated. The question is, how to minimise the refrigerant charge of refrigeration and air-conditioning units/systems?
Relevant answer
Answer
I am creating some eTools based on cloud platform and cloud computing for product designs and services. If you are design or service engineer, what eTools do you want to have on your smartphone or laptop?
  • asked a question related to Refrigeration & Air Conditioning
Question
8 answers
For 165 lit domestic refrigerator how much amount of refrigerant should i charge so that it will give better performance. 
Relevant answer
Answer
this link is very useful for your question
  • asked a question related to Refrigeration & Air Conditioning
Question
6 answers
Dehumidifying air coils have been widely used for refrigeration and air-conditioning systems. Generally the moist air dehumidifying over the fin surfaces is complicated for modelling. Traditionally, log mean enthalpy difference (LMED) is widely used. Some new methods have come up recently. Compared with the LMED method, which new method is most reliable for the modelling?
Relevant answer
Answer
  • asked a question related to Refrigeration & Air Conditioning
Question
3 answers
I am working on a two-stage refrigeration system with an economizer and ammonia as refrigerant. I have selected the equipement needed, and now I should choose the right piping and plumbing fitting and place them on my circuit. Since it's my first time working on this kind of project I would like to know the steps that I should be following to do so.
Relevant answer
Answer
Thank you Mr. Abdalla for your information !
  • asked a question related to Refrigeration & Air Conditioning
Question
5 answers
Generally pre-heating, humidification , re-heat used in Winter A/C. Whereas cooling coils in Summer A/C i.e. a single de-humidification process
Relevant answer
Answer
This is because winter air-conditioning demands heating and humidification.
Dr DB JANI
  • asked a question related to Refrigeration & Air Conditioning
Question
4 answers
Is it possible to measure the relative humidity accurately using a capacitive sensor for a cyclic change in input humidity and temperature (non-isothermal conditions, cycle duration is less than 60s)?
Relevant answer
Answer
Resistive-type relative humidity sensors: Resistive-type sensors are composed of interlocked metal electrodes that are deposited on a substrate. The resistance, which is measured by the sensor, decreases as the humidity increases. The advantages of resistive type sensors include being generally accurate in high relative humidities (>95% RH). it is not accurate for HR<15% (opposite to capacitive). Both capacitive and resistive types are affected by the variations of RH and temperature and the deviations between the measured and the actual values depend on the accuracy, sensitivity and the range of the model type. It was proved that the resistive type is more accurate within the specificed range of measurements and both types show a sensitivity for both RH and T.
  • asked a question related to Refrigeration & Air Conditioning
Question
9 answers
It looks that the fluid flow channel size of heat exchangers is becoming smaller and smaller. The widely used air coil heat exchangers for refrigeration and air-condioning, for example, use copper tube OD from common 19mm, 16mm, 12mm, 10mm, now to 8mm, 7mm, 6mm, 5mm and even down to 4mm and 3mm. In addition, more and more micro channel heat exchangers have been used for commercial and household products. Two questions:
1) Is it theoretically reasonable with thermodynamics to have the saying "the smaller, the better"?
2) Are we going to use micro channel HXs only or use normal/small/mini/micro channels combined HXs in a fairly large thermal system in the distant future?
Relevant answer
Answer
Hello, it's a interesting question and I'd like to share my opinion on it.
I don't think "the smaller, the better" holds for the generic heat exchanger.
The smaller size will increase the surface-to-volume ration, which helps increase the heat transfer surface area A. However, the heat transferred is determined by Q=hAΔT. Once you decrease the tube size too much, the flow inside the tube will turn from turbulent to laminar flow, and the heat transfer coefficient h will suffer from a huge loss. As a result, the final performance is the determined by the trade-off between h and A. So it's hard to conclude "the smaller, the better".
  • asked a question related to Refrigeration & Air Conditioning
Question
5 answers
I wonder if one has a table of quantities of refrigerants by weight for charging house hold refrigerators ranging between 10 - 20 cubic feet capacity. Is the charge the same if different refrigerants are used?
Relevant answer
Answer
Yes, we can find out the optimum charge mass of refrigerant in a domestic refrigerator/freezer and air conditioner to achieve optimal energy efficiency and/or capacity at a certain ambient condition range for a specific unit. The charge amount is decided by the refrigerant vapor and liquid ratio in components and the internal volumes of each components including the evaporator and condenser coils, filter internal void, liquid pipe volume, and compressor lubricant oil type. Proper charging is key to a product running safety and performance.
We have e-Tools to help estimate the optimal charge quantity of a CAP tube, TEX, or EEV refrigeration/AC unit available at the website www.refriglab.com. Both smart phones and laptop/desktop computers can work friendly with the website.
For unit services, it is always right and necessary o check the product brand plate/manual to get the proper charge amount. Remember that overcharge may damage your compressor, and undercharge will decrease the output of the unit.
  • asked a question related to Refrigeration & Air Conditioning
Question
5 answers
Manufacturers use capillary tubes for upper cooling by changing the diameter and length of the capillary tube. But I don't know the good diameter and length of the capillary tube for an air conditioner with 500w cooling capacity!
Relevant answer
Answer
With CapS/e-Tool at www.refriglab.com, CAP tube contacting factor=0 for detached/separate, =1 for common winding on, =2 for tube-in-tube arrangement with suction line pipe. Contacting Factor varies from 0 to 1.5 for winding on suction line to stand for different contacting degree.
  • asked a question related to Refrigeration & Air Conditioning
Question
4 answers
Wet bulb temperature can be measured by wrapping the senor with a wet wick, however, this method is subjected to high uncertainty. I search for a better method for this measurement.
Relevant answer
Answer
Dear / Alaa Al-Badri
Please try to use the hygrometer. The simplest hygrometer - a sling psychrometer - consists of two thermometers mounted together with a handle attached on a chain. One thermometer is ordinary. The other has a cloth wick over its bulb and is called a wet-bulb thermometer. This instrument in not expensive as well as it is more effective.
  • asked a question related to Refrigeration & Air Conditioning
Question
8 answers
Hello.
Thank you for your attention to this topic.
Is there a model for considering inefficiencies of different parts of a refrigeration cycle? for example something like we have about compressor?
Relevant answer
Answer
Dear researchers,
In the following publication from our research group all of the irreversibilities of the cycle were modeled:
  • asked a question related to Refrigeration & Air Conditioning
Question
4 answers
We use 4A zeolite molecular sieves in refrigeration application. now we want to regenerate this sieve in simple muffle furnace? what will be regeneration cycle. Please suggest most simple way.
details information of sieve is attached. 
Relevant answer
Answer
Regenerate 4A molsieve at ~250 deg-C. How long you need to regenerate it for depend on the amount of moisture/water adsorbed on it.
In a lab setup you can weight your sieve every 1 to 2 hours. When the reach a constant weight stop and cool it down gradually.
Keep in mind the sieve will lose some of its activity after regeneration.
  • asked a question related to Refrigeration & Air Conditioning
Question
4 answers
I want to analyze in the Fluent program in which R600a refrigerant will pass in thin pipes. There is boiling in a refrigerant. 
Relevant answer
Answer
How can I define R600a refrigerant in Fluent. is it need udf?
I want simulate heat transfer with assumption that R600a be ideal gas?
  • asked a question related to Refrigeration & Air Conditioning
Question
6 answers
Eg. which ones in supermarkets, which ones in domestic A/Cs or refrigerators, which ones in ice/brine production in industries, etc. segments
We will be phasing out some refrigerants. So, which technologies are ready with us as of now? Whats the issue with other refrigerant use? How are we dealing with this?
Relevant answer
Answer
There is an increasing interest towards R1234yf and R1234ze to replace R134a, in spite of their low flammability.
  • asked a question related to Refrigeration & Air Conditioning
Question
3 answers
In plant factory how Collection and reuse system of water condensed at cooling panel (evaporator) of air conditioners DONE?
Relevant answer
Answer
Spray the drain water on condensing coils , it will improve the condenser performance.  
  • asked a question related to Refrigeration & Air Conditioning
Question
3 answers
I am trying to simulate a specific type of an Absorption machine under Trnsys, the machine is a Yazaki 17.6 kWcool.
My question is how can I create a parametric file of the Type 107 to meet the performance of my AB machine ?
Relevant answer
Answer
I'm having the same problem, the external performance data for modeling the absorption chiller using Type 107 requires:
- Part load fraction to chiller
- inlet hot water temperature
- Inlet water temperature to the evaporator 
- Inlet cooling water temperature 
I think the absorption chiller you mentioned above is the Yazaki WFC SC5, for this and other size, the manufacturer defines the performance of the chiller using the last three parameters, nothing about the part load fraction chiller.
To be more specific in the manufacturer datasheet is shown the effect of water inlet temperature and hot water generator inler temperature on the design heat input and chilling power factor, giving the fraction of design heat input and the values of fraction of related chilling capacity.
What I'm trying to create is a simple model that allows to predict Yazaki's performance using the equations for the absorption chiller heat balance.
  • asked a question related to Refrigeration & Air Conditioning
Question
3 answers
I am comparing thermal stratification of different oils using thermosyphon charging
  • asked a question related to Refrigeration & Air Conditioning
Question
5 answers
I have seen the filter dryer is used in the cooling system for refrigerant part in between the condenser and expansion valve. Is there any water formed inside the tube when there is cooling process?
Relevant answer
yes there is always a chance of leakage.....
.
.
and the solid i am talking about can be anything but most probably solidified working fluid....
  • asked a question related to Refrigeration & Air Conditioning
  • asked a question related to Refrigeration & Air Conditioning
Question
9 answers
hello all,
I have this question  about the design as mentioned above. The capacity of refrigerator is  5TR and the evaporator temperature is 2 degree Celsius. also I need to compare the results for  at least 3 different refrigerants.
Do I have to use any software for this? If yes, can anyone help me with the names of software and procedure to use? If the software is not required, then what is the procedure to carry out calculations on paper? Please help me out with this.
looking forward to quick answers as I have a time limit to carry out calculations.
Relevant answer
Answer
You can use various commercial software's available ...you can also do in  MATLAB ( in order to study the effect of diff refrigerant.). but my advice would be that you should do programming in C rather than that pen and paper stuff...make your program more of user defined like ...properties of referigerants which he will enter....this would be best and most easier stuff as per your current state...
  • asked a question related to Refrigeration & Air Conditioning
Question
2 answers
I've come to build an experimental model for  impingement cooling system with corrugated sheets system that have a number of nozzles.
Can anyone help me to build a mathematical model for impingement cooling with corrugated sheets  system?
  • asked a question related to Refrigeration & Air Conditioning
Question
2 answers
Hi
I want to calculate monthly heating and cooling coil load in HAP software. How can I do? You know if I choose CAV in system, Heating coil load will be zero. Also if I use dual duct, then I have central heating coil load but even in cold hours, heating load is less than cooling load. Why it happen?
regards
  • asked a question related to Refrigeration & Air Conditioning
Question
4 answers
For better heat and mass transfer , which configuration of heat exchanger is best in adsorber bed for adsorption refrigerator/chiller. 
Relevant answer
Answer
Shell and tube exchanger has relatevely the best heat exchanging rate form contact surface area,thermal mass flow rate and configration point of view. However the effect of design style of chiller has certain effects and this may be taken into consideration.
  • asked a question related to Refrigeration & Air Conditioning
Question
7 answers
Relevant answer
Answer
In a throttling process if there is a change in phase say from liquid to vapor as in refrigeration cycles definitely the temperature will change from condenser temperature to evaporator temperature otherwise refrigeration process will not take place.
  • asked a question related to Refrigeration & Air Conditioning
Question
6 answers
I am asking this question because Joule Kelvin effect is in many a books related with gas expansion and not liquid expansion
When it comes to liquid expansion it is said throttling also an isenthalpic process like joule kelvin effect
Is Joule kelvin effect applicable to fluid and not only the gas
Relevant answer
Answer
Take a look to a T-s diagram of a refrigerant: you'll find that isoenthalpic transformation from saturated liquid have a negative slope, leading to a lowering in temperature for non-reversible adiabatic transformations. 
Another way to understand it is that during throttling liquid pressure lowers but as it is at boiling point these leads to some evaporation, as the process is adiabatic, transition heat is obtained thorugh a lowering in fluid temperature down to boiling temperature at the lower pressure.
  • asked a question related to Refrigeration & Air Conditioning
Question
3 answers
How can we provide optimized flow rate of heat transfer fluid to adsorber bed in adsorption chiller ?. 
Relevant answer
Answer
You should do energy balance based on the required temperature for your process.
  • asked a question related to Refrigeration & Air Conditioning
Question
10 answers
Hi everyone,
I have to prepare a lab set-up for a simple experiment with heat pipes, using butane as refrigerant. I need a pump for this refrigerant, suitable for small flows and pressure differences from 2 bar to 10 bar. Can anyone recommend the correct type of pump for this application?
Thank you in advance,
Valeria
Relevant answer
Answer
You will probably find good options from Micropump gear pumps (http://www.micropump.com/product_list.aspx?ProductFamilyID=5) and hydracell (diaphragm pumps) http://www.hydra-cell.com/product/F20-hydracell-pump.html
  • asked a question related to Refrigeration & Air Conditioning
Question
1 answer
The sample solution from the syringe goes in many direction after switching on the system. Is there any way to make sure that the sample will directly reach to the drum collector without getting wasted?
Relevant answer
Answer
I see this question for a while and wait for a answer from others, but still not. One possible reason is that people don't understand some words. I search 'espin method' but no source. If you can show a configuration of the system, we might be easy to follow. So far, I can only guess that your injector doesn't work well.   
  • asked a question related to Refrigeration & Air Conditioning
Question
5 answers
What is the impact on heat duty of condenser or any heat ex-changer if it is over designed?
Relevant answer
Answer
If a heat exchanger is overdesigned, heat duty will increase, resulting in higher coolant exit temperature and lower hot fluid exit temperature. For a condenser, provided that the vapor mass flow rate  is limited/constant, the condensing vapor pressure will decrease and the heat duty remain almost unaffected.
  • asked a question related to Refrigeration & Air Conditioning
Question
5 answers
As part of my studies,i need to write a MATLAB code to plot P-H chart of R134a Refrigerant.
I am trying to get the Mathematical equations using notion departure functions (correct me if i am wrong) but finding difficulty to get,as i don't have enough experience in it.
It would be really helpful, if some one could help me.
I am looking forward to hearing from you.
Regards
venkat
Relevant answer
Answer
You can use EES program, It is really a very good solution.  
  • asked a question related to Refrigeration & Air Conditioning
Question
2 answers
I'm searching to know the maximum power output of TEG modules per square centimeter (cm2).
Please send me the most up date information, including  the maximum power output of TEG modules (per cm2), working temperatures (hot side and cold side, delta T) and the corresponding TE materials.
Or, kindly suggest me a more recent research work, which may contains those information.
Many Thanks in Advance.
Relevant answer
Answer
The maximum power output is attained by differentiating the power output W
 in Equation (23) in the attached file with respect to the ratio of the load resistance to the internal resistance and setting it to zero
Please read the attached file
o
  • asked a question related to Refrigeration & Air Conditioning
Question
6 answers
new product of refrigerator used petrol instead of  R 12 and R 22 . 
Relevant answer
Answer
Dear Khaleel
Using hydrocarbonic gasses as refrigerants is still in R&D and its cost approach to the ordinary refrigerants today but in the next five years I think it will be more commercial than these refrigerants.
Regards
  • asked a question related to Refrigeration & Air Conditioning
Question
3 answers
The goal is to cool a 400-liter tank of 15 degrees Celsius water down to 5 degrees Celsius in about 30 minutes.
Most of the information I have found so far is geared towards refrigeration cycles for cooling air. Is it any different when cooling water instead of air? Can an evaporator be submerged in the water or will a custom evaporator need to be built?
Any help is appreciated, thanks!
Relevant answer
Answer
Hi, Cody:
I think submerged evaporator should not be a problem in terms of technical feasibility, after all it is already used in most air source heat pump domestic water heater on the market. Indeed, for most air source chillers, they do use evaporator to  generate chilled water. The only difference here is they do not store the chilled water in tank, they circulated the chilled water in a loop.
Best,
Chuan
  • asked a question related to Refrigeration & Air Conditioning
Question
7 answers
what are the steps to be followed for designing a CACA type heat exchanger for air to air cooled Generators/ Motors
Relevant answer
Answer
Designing a CaCa cooler is not done step by step but is a complete calculation. The maximum dimensions of fans for the external air is very often the start of the calculation. Is sound silencing nessecary? This gives extra pressure loss resulting in less air for the cooler. We design and build these CaCa coolers a lot in all kind of different designs. If you have more information what you are looking for please send.
  • asked a question related to Refrigeration & Air Conditioning
Question
4 answers
I make a review about this technology 
Relevant answer
Answer
Hi Kevin
Thank you very much Kevin for your assistance. I know that you left Edinburgh. I hope that everything going are excellent. my best
  • asked a question related to Refrigeration & Air Conditioning
Question
13 answers
??
Relevant answer
Answer
The evacuated tube collectors have an outer and an
inner casing of borosilicate glass 3.3. These tubes are
sealed at each end and between them a vacuum is maintained
to allow minimal heat loss due to radiation from the
absorber plate. As solar radiation is incident on the outer
layer of the borosilicate glass tube, a part of it is
absorbed, part reflected back into the atmosphere and
most of the radiation is transmitted to the next layer of
glass tube. The properties of the outer borosilicate tube
are given in Table 2. This arrangement is shown in Figure
2. Since,
τ = 0.92
α = 1- 0.92 - 0.04 = 0.04
From the empirical relations, the insolation at Dubai’s
latitude and longitude incident on a horizontal collectors is
measured to be approximately = 8.35 KWh/m
2
day. Figure
3 depicts a typical solar radiation curve over a clear day.
The readings on the graph are been plotted every 15 min
to obtain accuracy and correctness of the readings. The
graph clearly explains the gradual rise and fall of the
intensity levels of radiation. The area under the curve of
this graph gives the value in KWh/m
2
day as radiation is
only available from 7 AM to nearly 7 PM depending upon
the season. The data calculated indicates a value of 8.35
KWh/m
2
day incident in Dubai, it represents the entire
area under the curve of the Figure 3. To obtain the peak
value of insolation, it is required that this value is divided
with an approximate number of bright sunshine hours.
Assuming that May 15 is a clear day with no clouds and
8 h of bright sunshine, the radiation received/m
2
at every
incident would be = 8.35/8 ~ 1050 KW /m
2
. The further
calculations are based on this value of incidence solar
radiation flux.
G α sun = αlow temp σ (T
4
– T
4
surr)
Assuming the value of α sun = 0.12 as given in Rai (2009),
and the Tsurr= 40°.
The temperature of the outer glass plate is calculated to be 232C
  • asked a question related to Refrigeration & Air Conditioning
Question
3 answers
Hello,
Is it possible to use Thermolib to model an adsorption cooling / adsorption air conditioning process? I know that Thermolib has pre-built blocks for evaporator and condenser, and can be used for modeling the absorption process, but what about adsorber and desorber for adsorption process? Are they also built in, or do they have to be created? If they have to be created, then what is the procedure?
I would like to know before I purchase the software, so I would appreciate any help.
Thank you
Relevant answer
Answer
I want to model an adsorption air conditioning process with zeolite and water. I want to study how the temperature varies throughout one cycle of the system. Using Thermolib, I can model the evaporator and condenser, but how can I model the adsorber and desorber?
  • asked a question related to Refrigeration & Air Conditioning
Question
15 answers
In a domestic refrigerator, we generally use a hermetic compressor. The pressure lift or pressure ratio of the compressor is always maintained at a constant level or is it varying with the ambient temperature? Since higher ambient temperatures will lead to higher saturation temperature and pressure of the refrigerant, what is the role of compressor in this regard?. The discharge pressure is independent of ambient temperature or it varies with ambient temperature?
Relevant answer
Answer
Dear Vipin Nair,
First of all, domestic refrigerators use capillary expansion devices to create a flow restriction, not expansion valves. The capillary does not adjust the restriction according to the demand as pressure or thermostat valves.
Second, most of the domestic refrigerators have a ordinary On/Off compressor (NOTE: there are many available in the market with variable speed), which means when is powered on the compressor run in one speed only.
Considering those two conditions, yes, the compressor ratio varies according to the ambient temperature. This logically implies in variation of discharge pressure with ambient temperature.
There isn't much that the compressor can do when the ambient goes from cold to warm, besides keep pumping gas. See, the compressor will build a gas flow and a positive pressure difference. But the flow and pressure restriction is controlled by the circuit, mainly by the expansion device (in this case, capillary tube).
So, in the overall, when the refrigerator is running on summer, the pressure ratio is bigger (bigger condensing pressure, small change in evaporating pressure) and the compressor have to run longer time (because the thermal load in the cabinet is bigger, and the temperature difference between evaporator and cold compartment is smaller). In winter, the pressure ratio is smaller (smaller condensing and evaporating pressure) and the compressor run short time (small thermal load in the cabinet and big temperature difference between the evap. and cold compart.)
Keep in mind here that the cooling compartment temperature has the same set point in both cold or warm ambient.
Any doubt feel free to contact me.
Regards
  • asked a question related to Refrigeration & Air Conditioning
Question
11 answers
Considering laminar flow under constant heat flux boundary condition, we can find the average heat transfer coefficient as follows:
Average heat transfer coefficient = (Heat flux)/(Tw-Tref)
where, Tw=Average wall temperature
and Tref=Reference or bulk mean temperature. 
How to estimate Tref using FLUENT?
Thanks in advance
with regards
Relevant answer
Answer
Dear Nilesh:
You can plot or tabulate from Fluent the local heat transfer coefficient h(x) for example in the direction of flow, then numerically integrate these values to get the average heat transfer coefficient. For Tref in your equation, this is the bulk mean temperature of the fluid that is could be the arithmetic mean between inlet and exit.
  • asked a question related to Refrigeration & Air Conditioning
Question
3 answers
Some countries like Malaysia faced with hot climatic conditions that might affects the gas turbine performance. Besides fogging method, does anyone know what is another alternative ways to overcome this issue?
Relevant answer
Answer
Look at this doc it may be helpful for you topic. Good luck
  • asked a question related to Refrigeration & Air Conditioning
Question
5 answers
When is air is expanded in isentropic process temperature, pressure and enthaply decreases, but what happens in isenthaplic expansion enthaply remains constant but the pressure and temperature decreases or not. Mainly i need to know whether the temperature decreases or not.
Relevant answer
Answer
To find out whether air temperature lowers in an isenthalpic expansion you may use a state diagram of air. As enthalpy is a state property the final temperature will depend on final pressure and density regardless of the process. Be careful to check whether the process is really isenthalpic, evaluating especially kinetic energy: if inlet and outer ducts of a throttling valve have the same area kinetic energy at the outlet will be higher than at the inlet thus enthalpy will be lower
  • asked a question related to Refrigeration & Air Conditioning
Question
1 answer
Please speak about commercialized systems and not about the test/research setups
Relevant answer
Answer
Look at this doc please it may be helpful for your topic. Good luck.
  • asked a question related to Refrigeration & Air Conditioning
Question
8 answers
What is the lowest Delta_P , for capillary tube in refrigeration . Can capillary works under vacuum Condition i.e Condenser Pressure 50 kPa and Evaporator pressure 10 kPa ?
Relevant answer
Answer
And don't forget to see if the cappilary can hold the pressure difference. According to the mechanical of material, the stress due the pressure is calculated by: s = p.r/t (normal stress equals to pressure times radius divided by thickness). Use the maximum pressure difference between internal and external environment.
  • asked a question related to Refrigeration & Air Conditioning
Question
6 answers
This cooling may be droplet water cooling and also the key energy considerations for evaporative cooling system design. Moreover the most  promising areas for technology development in evaporative cooling system can be discussed. 
Thank You
Relevant answer
Answer
Thank you D.B. Jani
  • asked a question related to Refrigeration & Air Conditioning
Question
5 answers
I want to choose a compressor for my refrigeration system. I want to compress my refrigerant gas from 1atm to 6atm. How can I select a compressor for this duty?
Relevant answer
Answer
compressors basically divided into two categories
1-positive displacement
2-rotodynamic 
  • asked a question related to Refrigeration & Air Conditioning
Question
3 answers
Heat is gained through the glass window in a AC room. How can I calculated its effect on the power consumed by the AC?